Boiler / Plumbing Question


phantom

Recommended Posts

  • Admin

I had a problem with the water pressure being too low on my boiler yesterday, so increased this (but probably too high)

When I woke this morning I have noticed that my overflow pipe has water flowing out of it

Does anyone have any suggestions how I can stop it?

Would lowering the water pressure help - if so how do I do that?

I have tried getting a plumber but none currently available

Link to comment
Share on other sites

4 hours ago, phantom said:

I had a problem with the water pressure being too low on my boiler yesterday, so increased this (but probably too high)

When I woke this morning I have noticed that my overflow pipe has water flowing out of it

Does anyone have any suggestions how I can stop it?

Would lowering the water pressure help - if so how do I do that?

I have tried getting a plumber but none currently available

Hi Mark,

In principle, both hot and cold water have an identical pressure, but, just as a hot water storage tank may leak via the top inlet (due to rust etc.), reducing the temperature seems to reduce the 'pressure' and, consequently, the leaks.

I found with an old hot water storage tank that the leaking joint no longer leaked when I reduced the temperature, e.g. in summer or during prolonged absences.

I am sure any plumbers reading this will be able to explain the technicalities, but perhaps give it a try.

Good Luck.

Edited by PHILINFRANCE
  • Thanks 1
Link to comment
Share on other sites

4 hours ago, phantom said:

I had a problem with the water pressure being too low on my boiler yesterday, so increased this (but probably too high)

When I woke this morning I have noticed that my overflow pipe has water flowing out of it

Does anyone have any suggestions how I can stop it?

Would lowering the water pressure help - if so how do I do that?

I have tried getting a plumber but none currently available

Do you have a combi boiler ? Sounds like you have a problem with the expansion vessel, you can release pressure at a radiator air vent, catch the water in a bowl. Get it to about 1.2 bar when cold. Put the heating on and if pressure rises significantly its a faulty vessel or vessel needs recharging. Depending on make of boiler vessels are about £120 plus a couple of hours labour. The pressure relief valve has obviously opened so that may need replacing, if it's a Worcester that is a horrible job !!!

  • Like 1
  • Thanks 1
Link to comment
Share on other sites

  • Admin
15 hours ago, Frenchay Red said:

Silly question, but presumably when you opened the cold water flow to increase the pressure at the boiler, I assume that you then completely shut off the cold feed?

I didn't at first but noticed later that I hadn't

Plumber here now so should be sorted soon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...